ADN4605 channel status registers
I am able to access ADN4605 device and can access all the registers. But all the channel registers are showing 0x3F. I did not understand this issue? Is it software or Hardware issue?
i2c write at address 0x0 data 0x1
i2c write at address 0x0 data 0x0
i2c read at address 0x1d
channel 25 map 0 status should be 0x19 = 0x19
i2c write at address 0x2 data 0x0
i2c write at address 0xba data 0x0
i2c read at address 0x2
map select reg =0x0
i2c read at address 0xb0
tx enable reg before programming =0
i2c write at address 0xb0 data 0x3
i2c write at address 0xb0 data 0xf
i2c write at address 0xb0 data 0x3f
i2c write at address 0xb0 data 0xff
tx enable reg =0xff
i2c write at address 0x4 data 0x25
i2c write at address 0x5 data 0x24
i2c write at address 0x6 data 0x26
i2c write at address 0x7 data 0x23
i2c read at address 0x4
output channel 0 status =0x25
i2c read at address 0x5
output channel 1 status =0x24
i2c read at address 0x6
output channel 2 status =0x26
i2c read at address 0x7
output channel 3 status =0x23
i2c read at address 0xbc
i2c write at address 0xbc data 0x0
i2c read at address 0xd1
i2c write at address 0xd1 data 0x0
i2c read at address 0xc8
i2c write at address 0xc8 data 0x40
i2c read at address 0xc9
i2c write at address 0xc9 data 0x1
i2c write at address 0xc9 data 0x5
i2c write at address 0xc9 data 0x15
i2c write at address 0x1 data 0x1
adn update status =0x0
i2c read at address 0x54
channel 0 status 0x3f
i2c read at address 0x55
channel 1 status 0x3f
i2c read at address 0x56
channel 2 status 0x3f
i2c read at address 0x57
channel 3 status 0x3f
i2c read at address 0x58
channel 4 status 0x3f
i2c read at address 0x59
channel 5 status 0x3f
i2c read at address 0x5a
channel 6 status 0x3f
i2c read at address 0x5b
channel 7 status 0x3f
i2c read at address 0x5c
channel 8 status 0x3f
i2c read at address 0x5d
channel 9 status 0x3f
i2c read at address 0x5e
channel 10 status 0x3f
i2c read at address 0x5f
channel 11 status 0x3f
i2c read at address 0x60
channel 12 status 0x3f
i2c read at address 0x61
channel 13 status 0x3f
i2c read at address 0x62
channel 14 status 0x3f
i2c read at address 0x63
channel 15 status 0x3f
i2c read at address 0x64
channel 16 status 0x3f
i2c read at address 0x65
channel 17 status 0x3f
i2c read at address 0x66
channel 18 status 0x3f
i2c read at address 0x67
channel 19 status 0x3f
i2c read at address 0x68
channel 20 status 0x3f
i2c read at address 0x69
channel 21 status 0x3f
i2c read at address 0x6a
channel 22 status 0x3f
i2c read at address 0x6b
channel 23 status 0x3f
i2c read at address 0x6c
channel 24 status 0x3f
i2c read at address 0x6d
channel 25 status 0x3f
i2c read at address 0x6e
channel 26 status 0x3f
i2c read at address 0x6f
channel 27 status 0x3f
i2c read at address 0x70
channel 28 status 0x3f
i2c read at address 0x71
channel 29 status 0x3f
i2c read at address 0x72
channel 30 status 0x3f
i2c read at address 0x73
channel 31 status 0x3f
i2c read at address 0x74
channel 32 status 0x3f
i2c read at address 0x75
channel 33 status 0x3f
i2c read at address 0x76
channel 34 status 0x3f
i2c read at address 0x77
channel 35 status 0x3f
i2c read at address 0x78
channel 36 status 0x3f
i2c read at address 0x79
channel 37 status 0x3f
i2c read at address 0x7a
channel 38 status 0x3f
i2c read at address 0x7b
channel 39 status 0x3f
Attached is the schematics.
with regards
Dhananjay
vcgsm.pdf
  • Hi Dhananjay,
    I believe this may be a hardware issue. The software writes/reads look correct and the fact that you are able to read the correct values in some of the registers indicates that you are properly communicating to the device. I noticed on the schematic that the CSB pin is left floating. This pin gates the update so this needs to be pulled low in order for the XPT update to take effect. Please give this a try. I believe this should correct your problem.
    Jarrod
  • Hi Jarrod
    As per your suggestion, I pulled down chip select (CSB) as well as update pin. Still I see 0x3F in channel status registers.
      Please help me to debug this.
    with regards
    Dhananjay
  • Hi
      Is there any way to debug this board further?
    Dhananjay
  • Hi Dhananjay,
    have you solved the issue?
    I'm facing to similar one. Time to time I've seen wrong behavior, the writes go to the wrong register or read returns values from different or nonsense. I must admit it might be caused by problematic layout of the i2c bus on the PCB. Anyway it seems the switch (according to the scope) might responds with wrong values.
    Petr
    Apologies, I lost visibility to this thread as it was presumed to be answered correctly. With regards to intermittent behavior, can you please provide a scope shot of the I2C Data and Clock Lines? Have you verified that that register address and data on the scope are the same  as in software? Also, can you verify the logic levels of the I2C signals along with the DVCC supply voltage level? The ADN4605 will not internally write data to the wrong registers unless the data has been corrupted. This can be due to noise on the power supply (DVCC), improper power supply level, or incorrect control logic level. Other impairments can play a role as well, such as XTALK on the I2C bus. If you would like to share your schematic, I will be happy to review it.
    Jarrod
  • Hi Jarrod,
    Thank you for reply
    Yes, I've verified the i2c messages which comes from microcontroller are correct. Voltage levels seems to me correct (see below). I've also tried to repeatedly read the whole register set and compare it with stored one, what I've observed is that time to time the different value has been read. I've ended with correction task which compares registers with stored configuration and tries to correct errors, it runs until all reads are correct. So far this fixes all problems. Anyway it's kind of workaround.
    DVCC 3.3 V: noise 50 - 60 mV (switched power supply)
    I2C communication:
    I2C detail: ~50 kHz, 3.2 V hi level, small crosstalk on SDA
    See attached file for the schematic page (2.2k pull-up resistors for i2c are on another page).
    Thank you,
    Petr
    ADN4605_Schematic.pdf
  • Hi Petr,
    Thank you for the scope plots and the schematic. The power supply noise ripple of 50mV to 60mV is well within the supply tolerance range of +/-10%. The I2C voltage swing levels look correct. I do see XTALK on the SDA line. There is coupling from the SCL to SDA lines. It looks marginal on these scope plots, but if by chance the XTALK coupling was strong enough to create a gltich on the SDA line that is large enough to trip the mid level of the internal transistors (DVCC/2) then this could corrupt the I2C write/read and potentially generate a false start/stop condition. This could create the indeterminacy that you are experiencing. The plots you provided do not indicate that the magnitude of the SDA signal glitch is large enough to create this problem, but this could be dampened by the probe. It is something to look out for.  Other than this, everything else looks fine from a logic timing, level, and noise perspective. Can you please explain more about your correction task/workaround  and how it works? Do you just continue to write to the same register until you readback the correct value?
    Jarrod
  • Hello Jarrod,
    The cross talk between SCL and SDA is probably the main reason of wrong behavior. The probes damped the signal little bit as they have capacitance of 10 pF. Anyway I'm quite sad the chip sends nonsense (read as: data that is not in any register).
    The correction is relatively simple: After every change in configuration, the correction task is started. The correction task reads all registers in chip and compares read data with stored configuration, when mismatch is detected, the value in particular register is corrected and additional iteration of the correction task is requested. When all reads are correct, the correction task is stopped.
    The simple readback is not possible, because as I've observed, the value is rarely written to the wrong register, so whole register set check has to be done.
    Petr
  • HI,I   met the same problem.but when i pull  up the update pin i read the register(0x54-0x7b),reback 0x00-0x27,can u tell me  where is the debug?  it(0x54-0x7b) must reback 0x00 if there  are no prbolems?