Voltage at VOUT in shutdown mode
Product Number: LT8333
I would like to use the LT8333 to power my system.
I am using the circuit shown on page 23 of the datasheet:
Is it possible to put the LT8333 into shutdown mode by setting the EN input LOW and then apply an external negative voltage to VOUT to power the system without damaging the LT8333?
Thank you,
MaBo03
  • Hi Martin,
    You can shutdown LT8333 parts via the EN/UVLO by connecting a resistor divider to the input pin. However, you can not back-drive the LT8333 output pin with a negative voltage, as that will damage the IC.
  • Hello Tonyuche,
    thank you for your response. Could you please clarify which components need to be desoldered in order to apply an external negative voltage?
    Would removing D1 and R1 be sufficient, or would you also recommend desoldering L1A/L1B and/or C6?
    Where do you want to apply the external negative to? You can not back drive the IC, meaning you can not apply  external negative voltage to the VOUT. That will damage the IC, like I already explained.
  • Hi Tonyuche,
    please change the salutation in your last reply from Feb 18, 2026 12:36 AM to my community name MaBo03 and use this in future replies. Thanks.
    I use the LT8333 to power my system with a negative voltage Vout.
    For laboratory tests, I would like to apply the negative voltage Vout into the system via a negative external power supply and not from the LT8333 circuit (see picture in first post). For example, to measure the system current consumption or test other negative voltages, without having to reconfigure the feedback resistors or inductors of the LT8333 circuit.
    To avoid damaging the LT8333 with the reverse voltage injection, I could desolder components to isolate the circuit from the rest of the system for testing purposes.
    MaBo03
  • Hi MaBo03,
    Thanks for the name correction, accept my apologies..
    Regarding your question, you can turn off the IC by disconnecting the EN/UVLO from VIN, and either Ground it to TURN OFF the IC or connect a resistor divider to activate UVLO. After which, you can apply a negative voltage at the Vout and Isolate. Isolate L1A (desolder the sw end) , diode (desolder the anode), and the resistor (R1). That should isolate the IC.
  • Hi Tonyuche,
    thanks for your reply.
    On my PCB, it would be easier to desolder C6 instead of L1A. Would desoldering C6 also be a valid option to isolate the IC from the rest of the system?
    In addition, to further protect the IC from unintentional activation during laboratory operation, I am planning to connect SS to GND as well as EN/UVLO to GND. Would SS to GND additionally prevent the output of the LT8333 from being switched on?
    MaBo03
  • Hi MaBo03,
    The SS PIN is just for soft-start, connecting to ground and EN/UVLO would enhance the fast short down, since there is no external capacitor that is discharging from the SS pin via the internal MOSFET (M1). So, its fine you can connect both to ground.
    Regarding C6 is acting like output capacitor for flltering purpose. L1A is best option to Isolate. But you can leave it if you can not desolder it,  since the IC is off and the internal MOSFET (M1) will be off.
    I hope that helps.