Post Go back to editing

MAX17617A won't enable the output when it is loaded

Category: Hardware
Product Number: MAX17617A

It requires that the load is disabled before enabling the output otherwise it will not enable the output.  If the load is reduced to ~ <1A it will start.

SETUP:

Vin 48V,

CLMODE: 1K for continuous mode 0.5 ratio, and external

Rimon 5.3K

SETI: 5A

COUT 1320uF on board,

Enable control is a physical switch.

Using a Siglent SDL1020X Electronic load in CR (Resistance) mode (also tried CP mode).

Scope traces: C1 Yellow: VOUT, C2 Pink: IMon, C3 Blue Enable, C4 Green: Fault

Start with no load (just Cout)

Starting with load disabled but connected 

Starting the load

Start with load enabled.

The intended purpose of the circuit is to control current being supplied to a series of daisy chained radio devices on a single co-ax powered by DC bias on the cable.  The system is quite long at 3500-4000m, with significant v drop along the cable due to distributed loads.   I want the system to go into current limit if a cable fault or device malfunctions for diagnostic / fault finding purposes, and to protect devices on the network from overcurrent, and to be able to start under load in a fault condition.  Am I looking at the wrong device here.   Any hints as to why it won't start with the dcload?