Hi All,
I’m working on a power supply concept that can ride through short power interruptions using the LT8228.
Concept Overview:
Under normal conditions, 18 V is applied at V.
The LT8228 runs in boost mode, producing 56 V and charging a capacitor bank totaling 8.8 mF.
When 18 V is lost, the LT8228 reverses to buck mode, supplying the load from the capacitor bank.
Once 18 V returns, the LT8228 should switch back to boost mode.
The approach is inspired by the application schematic on page 64 of the latest LT8228 datasheet.
I’m using the EVAL-CN0556-EVZ evaluation board (see my setup below).
The switch is mechanical.
There is no load (i.e., R_load = ∞) during this test, giving ample time for manual switching..
5 Ohm resistor and diode in parallel makes the capacitor charging less problematic.
Modifications:
I’ve changed R1N, R2N, RUV1A, and CSS values to adapt the eval board to my use case, see bellow:
Observations:
With 18 V applied, the board properly switches to boost mode and charges the capacitor bank to 56 V.
If I open the switch (disconnecting V), it transitions to buck mode and supplies 14 V to V2 as expected.
Problem:
If I reapply 18 V while there is still residual charge on the capacitor bank, the LT8228 enters a persistent FAULT state pulsing.
Please see the oscilloscope capture below. Traces are Labelled.
Scope Details:
At the trigger point, I disconnect V — V2 drops from 18 V to 14 V (as FB2 is set for 14 V).
Shortly after reapplying 18 V, the FAULT pin begins pulsing continuously.
It never recovers, after ~46 FAULT pulses I manually disconnected V.
Below is a zoomed-in view of the FAULT onset:
In the plot below, I marked when FB2 crosses 1.3 V and 7ms window later (≈1024 cycles at the converter clock 146 kHz)
We see that after reapplying the 18V V2 starts going up, so does the FB2.
Expected vs. Actual:
According to the LT8228 datasheet, the device should switch to boost mode 7ms after FB2 > 1.3 V. Yet in this case, it enters FAULT instead.
Important voltages during the measurement above:
FB1 (V1 target is 56 V) is below 1.21 V. -
V1 under voltageset to 12.9 V, and the UV1 pin was above 1.21 V. - DRXN constant 3.3V
I think this behavior doesn’t align with the datasheet’s mode transition diagram.
Question:
Can anyone help explain why the LT8228 is entering FAULT after VIN is reapplied while the output caps are still partially charged?
Any insight would be greatly appreciated.
Thank you.
Edit Notes
Added DRXN voltage information[edited by: DimitarPenev at 1:57 PM (GMT -4) on 17 Jul 2025]