OR ring N+1 Redundant Circuit
Product Number: LTC4357
how to configure channel for differential signal input  - NTC 10K
As an illustration
1)What channel should be connected to the "+" and "-" side of the differential signal, respectively?
2) For the differential mode, is every "-" side channel connected to ground?
 We are using 2 individual PFE500F-12 (AC-DC) with two different source of AC 230V to 12 V and that two 12V 42A ORing for the one N+1 redundant 12V  is the Load for system. whether LTC4357 & SQM50N04-4M1_GE3 sufficient for 12V 40 A N+1 redundant.
  • 1)What channel should be connected to the "+" and "-" side of the differential signal, respectively?
    This ideal diode is intended for DC applications for power savings, not to rectifying AC signals.
    For high current applications, I recommend the LTC4359.
    It's floating topology protects the IC from abs max violations during input short and supply switchover.
    As for the FET, the SQM50N04-4M1_GE3 specs are: RDS(ON)=4.1mΩ with ΘJA=40C/W.
    Assuming one channel carries the entire 40A, you need at least 2 FETs in parallel for reasonable temperatures.
    TJ will rise 65C above ambient with 2 FETs in parallel.
    The temperature of the operating environment determines how much junction temperature can rise.