LTC3871 - HV system application
Product Number: LTC3871
I am looking into possibility of using LTC3871 as a bidirectional current controller in a higher than recommended voltage system (800V and around 200V). My main concern are inductor current sense channels, since they are optimized for direct shunt connection with range limited to ~50 mV. Are there any recommendations for current sensing circuit in such application? My first thought was current transducer with FDA circuit scaling transducer reading to appropriate range or isolation amplifier combined with FDA conditioning.
Is there anything I should also pay special attention to while using LTC3871 in this way? Or maybe LTC3871 is not suitable for this application? I was also planning to connect 2 LTC3871 to create 4-phase interleaved system.
Thank you in advance,
BN
  • Hello BN,
    VHIGH and VLOW voltages of 800V and 200V are too high for the LTC3871 as you noted. The 800V VHIGH limitation can be circumvented by biasing the LTC3871 with an external bias of 12V, preferably, and external gate drivers. However, 200V on VLOW presents a difficult challenge. The maximum VLOW voltage of the LTC3871 is 30V since the absolute maximum rating of its current sense pins is 34V. Using a resistor divider to drop the common mode voltage to 30V or below is not possible due to the 1.5mA input current of the SNS- pins and the large attenuation factor required (>7x). Using a high voltage difference amplifier may be a solution. However, the BW of the amplifier should be about 10x the switching frequency to allow the triangular portion of the current sense waveform to pass through. Otherwise, the current sense signal will be rounded and delayed. This can lead to stability issues. Since the LTC3871 is a peak current mode controller, the current sense signal is a critical part of the feedback loop. If you still need assistance with this circuit, then contact your local FAE.