Hi everyone,
I'm designing a flyback converter using the LT3757a to boost a 5V input to 170V:
With a 40mA active current load on the output, I'm getting a pretty clean output at 170V:
However, I'm seeing several issues on the other stages:
The input caps don't do anything after startup in terms of smoothing out the current spikes. I'm pretty sure this is a modelling issue where I haven't taken some parasitics into account, but I'm not sure how to fix this.
I specified a coupling coefficient of 1 for the inductors, so there shouldn't be any leakage inductance causing the oscillations.
If I could get some help with the design to either fix these issues or verify that this behavior is expected, I would appreciate it!
EDIT: so I found that all of these issues improved after increasing the inductance values in my coupled inductor. By changing them to 10uH/1000uH, the oscillations went away and the current spikes decreased to about 5A. Increasing the inductance values further reduced the current spikes on the input to about 3.5A, and further increased in inductance saw very little change.
I assume this indicates that my inductors were saturated, but I don't understand how the oscillations/current spikes relate to this.
Hallo Soohan,
your have an ideal voltage source in parallel to your input caps. As the ideal source keeps the capacitor voltage exactly constant, there is no current flowing in or out your input caps. Adding some internal resistance to your source (as it would be in a real voltage source) will change this.
You have choosen the switching frequency to be 100 kHz (by setting Rt to 140kOhm). So you have one single switching pulse every 10µs, and every single pulse needs a certain energy (and therefor a certain current) to provide the needed output power.The energy stored in your inductor is 0,5*L*I^2. You want an output power of 170V*40mA=6,8W, you need 68µJ per 10µs pulse. And 68µJ in an 1µH inductor means, that the current has to go up to almost 12A.
In simulation your inductor is not saturated, as your simulation model for the inductor does not know anything about saturation. In real life it would depend on your real inductor if it would stand these high current pulses without saturation.
You can change this by
- either increasing the inductance (you found this already).
- or increasing the switchting frequency (setting Rt to a lower value). You have choosen the lowest frequency specified for the LT3757. If you reduce Rt and increase the switching frequency, you get more pulses per time, and every single pulse requires less energy (less current) for the needed output power.
Besides that two more hints:
- I would recommend to use a "real diode" model for simulation instead ot the intrinsic model of D1
- you have build a low pass filter (R4, C4) in the current sense circuit. Depending on the switching frequency you finally choose this will mean, that you limit the average switching current, not the peak current. And this may be a bad idea, since the peak current may already be destructive while the average current ist still acceptable.
best regards
Achim
Achim,
Thanks a ton for your feedback, it was very helpful for understanding what was going on!
I've introduced the following changes to the design:
However, when I try to add a real diode model to replace the intrinsic model, I run into some issues.
I have simulated both in place of the intrinsic model, but for each one, I see the following changes:
The output voltage is able to reach the programmed 170V (I'm assuming the blanking period on the sense pin ignores those voltage spikes above 100mV)
Adding the LPF back to the sense pin did not resolve the issue. I'm pretty sure the compensation network/pin isn't involved here.
I don't understand how a change of the diode on the output could cause this. Any explanation would be appreciated!
Hello Soohan,
The realistic diode models include the effect of reverse recovery time.
When the transistor is off, the diode is forward biased and delivers current to the output. When the transistor is just starting to conduct, the diode gets backward biased and should block the current. But this does not happen immediately, the diode is still conducting in backward direction for some ns - the reverse recovery time. This is the short current pulse you observe and which was not modelled by the simple diode model.
best regards
Achim
Achim,
That makes sense, thanks for the explanation. My (hopefully) last question on this topic is: do I need to compensate for these spikes due to the reverse recovery time? With the diode I selected, they only last for around 25-50ns.
Is this something I need to clamp, or simply part of the switching losses/reduction in efficiency?
EDIT: Also, when I change the coupling factor of the inductors from 1 to 0.985 (to account for max leakage inductance), the current spikes on the primary side seem to disappear! Is the leakage inductance acting as a filter in this case?
Hello Soohan,
I don't think, there are good methods to compensate this current peak - it is indeed part of the switching losses. One may just look for better (faster) diodes, but your choice of RFN1LAM6S is already quite good. (it's promoted as Super Fast Recovery Diode). For lower voltages a schottky diode might still be better, but for your application the choosen diode is good.
Regarding the changes you observe with a more realistic leakage inductance: I'm not really sure if one can describe this with a simple, straight forward explanation.
best regards