LT4295 POE+ 66W Forward mode topology simulation
Hello AD Team,
We have designed LT4295 PoE++ 12V/5.5A forward mode converter by referring the datasheet typical application and DC2584A-1-A-SCH document. Attaching the schematic here.PFA
But the simulation result fails, as we simulate in LTSpice simulator. Output is not stabilizing but it goes down to zero as in the attached image.
Please provide your suggestion. Kindly indicate where it is going wrong.
Pradeep. S
Parents
  • +1
    on Sep 17, 2020 5:07 AM
    Hi Pradeep,
    You have the active clamp FET directly connected to the drain of the primary FET. The active clamp FET (driven by the SG pin) should only connect to the transformer through the RC circuit. You should also connect D9 to L11, instead of the gate of Q7. Give that a try.
    Best Regards,
    Eric
  • Hi Eric,
    Thank you so much for your suggestion.
    We have implemented the changes that you have suggested and simulated it again. Still the output is not ramping up to 12V. It is just fluctuating around 3V. Attaching the waveforms and simulation file. PFA
    Also requesting to check on the transformer inductance on both winding we have used is correct or not. We are not clear on the transformer winding inductance values. Kindly suggest us the primary secondary inductance values. Before output InductorITHB pinOutputPGSGsecondary winding bottom wire.Vcc pin4295_NEW_selva-Winding_002.asc
    Pradeep. S
  • Hi Eric,
    In LT4295 datasheet, the external inductor and capacitor required are specified as two options in Table-3. One for PoE mode operation and another for auxiliary operation.
    My design accepts both power modes. In this scenario, which inductor and capacitor value I need to take from the datasheet. Attaching the image of that.
    Kindly provide your suggestion.
    Thanks
    Pradeep. S
    on Oct 14, 2020 4:26 PM in reply to pradeepkumar.selvaraj@aricent.com
    Hi Pradeep,
    PoE voltage at the PD ranges between 37V and 57V, depending on several factors. A wide input auxiliary such as 9V to 57V includes the PoE operating range of 37V to 57V. If you are just operating off PoE or with an auxiliary that has the same 37V to 57V voltage range, then use the values in the bottom row. If you are using an wide input auxiliary, use the top row.
    Best Regards,
    Eric
  • Hi Eric,
    Thank you for your suggestion, we implemented it.
    And as from datasheet, Vauxon voltage level must be lower than VHSOFF = 31V. But we are designing the aux supply to take over at only 37V which is violating the above rule.Attaching the images. PFA
    If I have to adhere this rule, my board's primary transformer side power traces capability has to be increased which is not possible now. Requesting for your suggestion on this.
    Pradeep. S
    on Oct 30, 2020 11:01 PM in reply to pradeepkumar.selvaraj@aricent.com
    Hi Pradeep,
    I've answered this question in a separate thread.
    Best Regards,
    Eric
  • Hi Eric,
    Good Day!!! It has been after a long...
    With your guidance, we have successfully simulated LT4295 chip for obtaining 12V/5.5A output from either Auxiliary input 37-57V or PoE 37-57V inputs using DC2584A schematic.
    Now, we have another design requirement which has two ranges of lower auxiliary input voltages 12V/24V & PoE 37-57V & output of 12V, 25 Watts.
    We have modified the existing design with the below changes,
    • Tested as two cases with the below changes. Case1: Aux IN =12V & case2: AUX IN= 24V
    • Changing the existing forward mode transformer model (1.5:1 ratio) to the ones supporting lower primary input voltages (POE38PR-12E_ or 7491196212-1723807) having pri-sec winding ratio of about 1:2.115.
    • (This is done by changing the transformer model winding inductances as Primary inductance=128uH & Secondary inductance =578uH)
    • Adjusted the Auxiliary sense resistor divider value to required AuxON/AuxOFF thresholds.
    After the above changes, the simulation result is somewhat good, but having below observations, (attached the result images. PFA).
    Case 1 Observations:
    • 12V Output is oscillating around 11.4V to 11.8V, but not an exact 12V.
    • Output have ripples of +/-450mV .
    • Also I measured that PG pin duty is 60% and more...I understood from the datasheet that recommended duty should be around maximum of 53%. Is it okay??
    Case 2 Observations:
    • And for case2: AUX IN=24V, Output comes only around 9V.. My design should accept both 12v as well as 24V aux inputs.. what is the problem here? Anything to do with output inductor???  Please suggest Case2_Aux in 24V_9V only coming
    Case 3 _PoE powered:
    Also, the same result is coming for PoE mode operation as shown below. During PoE mode, I have changed the auxiliary input voltage down to 1V.
    Please help us to solve them & please provide the way of calculating the output inductor.
    Also please provide your kind suggestion that the way we have modified this design is right or not?
    Thanks & Regards,
    Pradeep. S
Reply
  • Hi Eric,
    Thanks & Regards,
    Pradeep. S
Children
No Data