KCC's Quizzes AQQ306 about a fish stick challenge
1. First the quote of the month: " I am so clever that sometimes I don't understand a single word of what I am saying" - Oscar Wilde
2. New quiz AQQ306 about a fish stick challenge:
Here below is a pseudo fish diagram swimming to the right.
Question
View All
October Monthly Blog Quiz! Read the blog, take the quiz, and you could win a gift card
Finding Your Circuit Chi — EMC Quiz!
Think you know EMC? Test your knowledge with our 5-question quiz!
Read the blog first, then take the challenge: Finding Your Circuit Chi
Every current flowing creates electromagnetic fields.
Strong EMC design
View All
ADM3066E
Production
The ADM3061E/ADM3062E/ADM3063E/ADM3064E/ADM3065E/ADM3066E/ADM3067E/ADM3068E are 3.0 V to
5.5 V, IEC electrostatic discharge (ESD) protected RS-485
transceivers...
Datasheet
ADM3066E on Analog.com

Hi,
I’m happy to help and would like a bit more information to better understand the issue:
This information will help us better pinpoint the root cause.
Best,
Jane
Hello!
Thank you very much. So,
1. No the bus during testing is only terminated at one end. The Master side. The other end is open.
2. Stub lengths are a few cm long, less than 10cm.
3. 24V and Ground is being passed on the same 4 core cable to the slaves. All grounds and supplies are connected to the battery with a lowside mosfet to be able to turn on and off the slaves. Both master and slave use a non isolated DC to DC converter to get 5V from 24V and an LDO for 3.3V. So there is no osolation between slaves and no isolation between supplies. Isolation between the 24V and low voltages is difficult here since there are a large number of 24V mosfet switches, which would need isolation. VCC and Vio are set to 3.3V.
4. The receiver of the IC is completely blown, never receiving any signals. Which other chips on the bus do. But the transmitter of the IC works fine. Thus I had to.change the ICs for the system to work again.
5. I will provide more info and sketches on 3 and 5 when I get to the lab.
Onve again thanks for your help
Find a simplified block diagram of the system setup. Look forward to your reply.

Hello, any updates?
Hi,
Sorry for the delay. Please ensure 120Ω termination is used at both ends of the main bus to maintain signal integrity.
To better understand your application, could you please help with the following:
Thank you for the additional information.
Best,
Jane
1. Yes, the master and the first slave receivers where both blown.
2. No Bus Protection scheme in place
3. Around 3 meters between damaged Master and damaged slave.
Does a high current being pulled by the slave on the supply cause ground potential differences?
Hi ,
High current can sometimes cause ground potential shifts, even over relatively short distances. Since the device and package are not designed to handle high current, a few amps will damage the part.
Under normal operation, the receiver should not carry significant current. We recommend checking for any short or transient events that could be stressing the device and adding bus protection on each module.
Hello, thanks for your response. We will try to implement protection.