Hello,
we have identified a specific measurement issue when varying the input frequency away from nominal 50 Hz / 60 Hz under low-amplitude input signals:
Test condition:
Voltage=5V; Current=0.0128A; Active power=64mW; PF=1; Frequency=52Hz
Test Result:
Vtotal=5.008V; Itotal= 0.0131A
Vfund=0.668V; Ifund= 0.0017A
PF=0.05
Observations
* RMS measurements (V_rms, I_rms) remain accurate. However, the fundamental RMS (V_fund, I_fund) become completely false.
* Voltage and current THD registers saturate at 400 (the maximum distortion limit measurable by the ADE9000).
* Consequently, the Power Factor collapses to ~0.05 instead of (PF = 1.0), leading to active power errors.
Are specific register configurations required to prevent low-amplitude fundamental signals from being filtered out as noise outside 50 and 60 Hz?