I am using the ADE7953 with the current sensing network shown in the attached schematic.
Configuration:
- Current shunt: 5 mΩ
- Input filter:
- R64 = 100 Ω
- R65 = 1 kΩ
- R55 = 100 Ω
- R54 = 1 kΩ
- C44–C47 = 22 nF
- AGND is connected to the line reference (non-isolated design), as recommended for this application.
- The relay is normally open.
Problem:
As soon as AC mains is applied, before the relay is energized, resistors R64 and R55 (100 Ω) burn immediately.
The relay is still OFF, so no load current should be flowing through the shunt.
Additional observations:
- I verified the shunt value (5 mΩ).
- The capacitors and resistor values are correct.
- I replaced the ADE7953 with a new device, but the problem remains.
- I built the same current sensing circuit on a prototype board and it works correctly.
- However, when I connect the sensing inputs (IA+, IA−, AGND) to the shunt on my PCB, the 100 Ω resistors burn again, indicating that the problem is related to the shunt/load side rather than the ADE7953 itself.
With the relay open, I measured approximately 220 VAC between the lower side of the shunt and AGND (Line reference), which is expected because the load is connected to Neutral.
Could you please advise whether this input network is correct for this topology, or if there is any recommended way to connect the current shunt when the relay is placed before the shunt?
The schematic of the current sensing circuit is attached.
Thank you.