Post Go back to editing

How do i setup the tdk current transformers with the eval ade9000 shield board?

Category: Hardware

Hi Analog Team,

I've acquired TDK CTs as per the Analog guide.

Please guide me on how to setup the CTs to the evaluation board. Would I just need to put the 3phase 4 current wires through the CT clamps while the CT do not need to be connected to the arduino zero, correct?

Looking forward to your kind reply.

Thank you very much.

Edit Notes

updated
[edited by: Nabil83 at 11:54 PM (GMT -4) on 15 Oct 2023]
Parents Reply
  • The current channel  ADC input is .707vrms  I would suggest half of fullscale or more for surge currents

    if you have 15a and a 1000:1 ct 

    (.707/2)(15/1000) = 23 ohms   I would divide this by 2 and use then as differential burdens as show in the diagrams I sent R1 and R2

    Replace the values for your ct ratio  and current and  you can calculate the burden value you need. 

    Dave