Need example to connect current transformer to ADE7933

Is there an example of how to connect the ADE7933 with current transformers?

Thank you

Fausto Bartra

Parents
  • Hi Fausto Bartra,

    The ADE7933 is an isolated ADC most typically meant for use with a shunt current sensor. If you are using a current transformer then isolation is already present in the transformer.

    Could you tell me more about the application? Maybe there is a more appropriate metering IC to choose from with use with CT's. Do you need to use CT's over shunts? Is this a 3-phase application?

    The maximum input level on the current channel is +/-31.25mV Peak, therefore a small burden would have to be chosen to not over range this input.

    Regards,

    Dlath

Reply
  • Hi Fausto Bartra,

    The ADE7933 is an isolated ADC most typically meant for use with a shunt current sensor. If you are using a current transformer then isolation is already present in the transformer.

    Could you tell me more about the application? Maybe there is a more appropriate metering IC to choose from with use with CT's. Do you need to use CT's over shunts? Is this a 3-phase application?

    The maximum input level on the current channel is +/-31.25mV Peak, therefore a small burden would have to be chosen to not over range this input.

    Regards,

    Dlath