When I connect scope to buffered excitation outputs - EXC and /EXC - I get unexpected signal ( sin/cos expected):
There are basically only halves of sin() signals. When I put probes in various parts of board I get these values - please note that EXC output from AD2S1200 looks correct (yellow wave):
Question: Is that buffer output correct? (I'm expecting normal sinusoidal output as is shown right at EXC PIN34 of AD2S1200).
This behavior was observed in both extreme cases:
- Just powered evaluation board with 9V power supply and only connected scope. No other connections made.
- Board powered, connected Resolved simulator card (to both Excitation output and SinCos inputs), connected via USB to PC and run AD2S1200_05
When I combine differential EXC and /EXC outputs together (using differential input on scope) they resemble sin() function, but not exactly - there is noticeable distortion.
Details on board and chip:
Board is: EVAL-AD2S1200/05SDZ Rev A
Chip on board is: AD2S1205 YSTZ
Added detailed board and chip specification.