AD7616 Burst Sequence in Serial Software Mode
Hello?
I looking for procedure of Burst Sequence. (1-wire Serial, Software Mode)
I want to set V0A-V0B-V1A-V1B-V2A-V2B-V3A-V3B-V4A-V4B-V5A-V5B-V6A-V6B-V7A-V7B.(and then loop-back)
I did for this list.
1. RESET High and Low
2. skipped input range setting.(using default +-10V)
3. setting seqencer stack channel
  - 0x20 ; 0, 0 (transmit 0xc000)
  - 0x21 ; 1, 1 (transmit 0xc211)
  - 0x22;  2, 2 (transmit 0xc422)
  - 0x23;  3, 3 (transmit 0xc633)
  - 0x24;  4, 4 (transmit 0xc844)
  - 0x25 ; 5, 5 (transmit 0xca55)
  - 0x26;  6, 6 (transmit 0xcc66)
  - 0x27;  7, 7 (transmit 0xce77)
4. Setting seqencer stack SSRENx bit
  - 0x20 ; 1 (transmit 0xc100)
  - 0x21 ; 1 (transmit 0xc311)
  - 0x22;  1 (transmit 0xc522)
  - 0x23;  1 (transmit 0xc733)
  - 0x24;  1 (transmit 0xc944)
  - 0x25 ; 1 (transmit 0xcb55)
  - 0x26;  1 (transmit 0xcd66)
  - 0x27;  1 (transmit 0xcf77)
5. CONVST Set High and Low
6. After read loop 16 word (16 bit x 2(A/B) x 8 times(0~7)) using transmit 0x0000
it is only read V0A / V0B 8 times each.
How to read normally at once?
Please reply.
Thank you.
adding tags
[edited by: Lluis at 4:06 PM (GMT 0) on 2 Dec 2019]
Parents
  • +1
    on Dec 2, 2019 4:16 PM over 1 year ago
    There are two things I want to note from your procedure above:
    -RESET line is active low, so you should tie it high when idle
    -steps 3 and 4 should be merged into one, i.e. you need to assert SSRENx only once. On the last channel within the sequence. So, you should have instead:
    1. Toggle Reset (and wait the required time). Make sure SER1W pin is low prior to the full reset
    2. Write the Sequencer stack registers:
      - 0x27;  7, 7 (transmit 0xcf77) SSRENx high, so it tells the device that this should be the last item on the sequence
    3. Bring DIN low and issue a dummy conversion
    4. Toggle CNVST and wait for BUSY line to de-assert
    5. Read 16bit * 2ADCs * 8ch while keeping DIN tied low and loop back to 4.
    I hope this helps.
    Lluis.
  • I've solved. The method was corrected, but my MCU had problem.
    Busy time for all conversions is about 7 us, after 16 bit * 16 sample load is O.K.
    Thank you.
    on Dec 5, 2019 12:48 PM 11 months ago in reply to Passerby2
    Glad to hear you manage to spot and resolve it.
    Lluis.
  • I forgot to fill in additional.
    1. Originally RESET was Low and High.(Active Low, fill in mistake)
    2. Conversion result is up and down 5 bit peak to peak for resistor of regulated voltage. It is difficult to decide whether it is good or not.
    3. Busy time is delay(about 7 us) at SPI 20 MHz. I will use it speed up to 40~50 MHz.
    Thank you.
Reply Children