AD9545 Eval Board 1PPS Setup
The user is facing issues configuring the AD9545 eval board to generate a 1PPS output. The final answer provides a detailed configuration guide, including the need for a real 1PPS generator and an OCXO at REFA to stabilize the DPLL. Key settings include using a 52 MHz crystal resonator, setting the REFB validation timer to 1000ms, and configuring DPLL0 and DPLL1 for internal zero delay and phase buildout. The user should also ensure the correct jumper settings for CML outputs and check the REFA AC coupled, single-ended specification.
Product Number: AD9545
I'm attempting to configure the AD9545 on the AD9545 evaluation board but hitting some issues with the 1PPS configuration.
I am using REFB to generate:
1) OUT0A = 156.25MHz
2) OUT0B = 1Hz
3) OUT0C = 10MHz
4) OUT1A = 100MHz
5) OUT1B = 100MHz
I amusing the on-board 52MHz oscillator as the system clock, but also have a custom board which uses a 48MHz oscillator.
I would like to evaluate my design on the AD9545 evaluation system before transitioning to my custom board.
I can generate all output clocks successfully when using a 10MHz clock connected to REFB as proof of concept.
I am trying to understand what additional settings are required for the 1PPS use case.
Based on what I have read on the forum, I must use a real 1PPS source rather than a 1MHz clock from a function generator - is this correct?
I have read many threads on the forums but am now somewhat confused about what to do next.
1) What value to use for REFB validation timer? 1000ms? Any other non-default settings?
2) What values to use for REFB Lock Detect settings? I see recommendations of 100 or 200 for fill/drain rates. What about Phase/Freq lock thresholds? I see 2000 recommended for Phase Threshold.
3) Do I need to enable Aux NCOs? If so what frequency and if one of both?
4) I have Auto Sync Mode and Ref Sync Enable set for both DPLL0 and DPLL1.
5) I have Phase Buildout, REFB and Loop BW of 50mHz for both DPLL0 and DPLL1.
6) What settings should be used for System Clock Compensation settings? I did not need this for the 10MHz case.
7) By modifying my 10MHz use case to 1PPS only modifying the input frequency, I can see REFB Valid, ACT (DPLL0/DPLL1) and LD (APLL 0/APLL1) LEDs greed, but not FLD/PLD (both DPLL0/DPLL1).
I believe that the main adjustments should be made to the above.
Note: I do not have any other Reference clocks available on my custom board - do I need to modify the board to include additional reference clock sources to successfully implement the 1PPS use case?
Declan.
    attached is a paper that explains how to set the AD9545 eval board (and consequently any board) to receive a 1PPS clock reference and create 1Hz clock in phase to the 1 PPS. I believe this paper answers a lot of your questions.
    7624.1PPS_control_with_AD9545_20241213.pdf
    Get the AD9545 eval board to function first and then you can move easily to your custom board.
    Other comments:
    - the AD9545 eval board uses a 52 MHz crystal resonator. This is different from an oscillator. You need to check the Xtal Source box in the Configuration Wizard. On your custom board, do you use a 48 MHz oscillator or a crystal resonator? When the time will come, just change 52 MHz with 48MHz and check or uncheck the Xtal Source box.
    - you need a real 1 PPS generator or a rubidium or cesium based signal generator to create the 1 PPS (or 1 Hz) reference clock
    - you also need a OCXO of a low frequency (10MHz or 20 MHz) to stabilize the effects of the crystal resonator wonder using the Auxiliary DPLL. Otherwise the DPLL will never be able to lock permanently onto 1 PPS.
    - on DPLL0, use Internal Zero delay with an internally embedded clock of 1 Hz onto OUT0C=10MHz.
    - on DPLL1, use phase buildout. If you want the 100MHz output to be in phase to the REFB=1PPS, set DPLL1 in internal zero delay mode, embed a 1 Hz into OUT1A (for example) and use OUT0A as feedback.
    I created a configuration that should work onto the AD9545 eval board if:
    - REFB=1Hz, 1.8V CMOS (read the paper because you need to change the board hardware)
    -REFA=10 MHz coming AC coupled from an OCXO
    -all outputs are CML, 15 mA. Make sure the jumpers P300, P301,..., P304 are between pins 1 and 2.
    Take out the txt extension before loading it into ACEAD9545_setup_20260818.cso.txt
    "Note: I do not have any other Reference clocks available on my custom board - do I need to modify the board to include additional reference clock sources to successfully implement the 1PPS use case?"
    Yes, you'll need to add the OCXO at REFA. I used 10 MHz, but you can put whatever frequency your OCXO has. Then make sure you chose an OCXO that, when you AC couple its output, the amplitude conforms with the REFA AC coupled, single ended, specification:
    Petre
  • Thanks Petre!
    Passing this along to the team now.
    I'll post an update here if we need any clarification.
  • Hi Petre,
    Can you confirm typo in Table 64?
    I believe the 4th entry should state "REFBB TDC" rather than "REFB TDC"?
    Declan.
    thank you very much.
    I confirm the change is for the bit code 00011 to select REFBB TDC. I have it noted, so when we'll decide to update the data sheet, this will be corrected.
    Petre
  • Hi Petre,
    Can you provide guidance on my current CSO?
    This has been provided by our HW team but unfortunately, it not possible for us translate directly from the eval board to our custom board as the references are swapped. I've attached the cso (changed to .txt) for reference.
    Also, for DPLL1 I get an error for the allowable frequency range even thought it looks to be correct at 1Hz (perhaps a rounding error) ?
    Declan.
    ad9545_20260910.cso.txt
  • HI,
    I looked over the cso file you sent. Do not worry a multiplexer in the GUI DPLL1 path is in red. It may have happened because of the different precision in the calculations of the multiplexer entries.
    As it is constructed now, it seems mostly correct to me. I found only some incongruencies:
    - why DPLL0 has a 50 mHz loop bandwidth when the reference clock is REFB=156.25 MHz? You should use 50 Hz loop bandwidth
    - why a 10 kHz loop bandwidth on AuxDPLL? Normally we use 50 Hz or max 100 Hz.
    - you also have to compensate the TDCs
    - you enabled AuxNCOs in the configuration wizard. Not clear why. If you plan to use them for some TDC reading, then compensate them as well in the AuxDPLL
    - Because AuxDPLL lockes onto REFB=156.25MHz, this must be a TCXO or OCXO. Why such a high frequency? A 10 Mhz or 20 MHz would suffice. Important here is the stability in time and accuracy of the TCXO/OCXO
    DPLL1 locks onto REFA=1Hz with a 50mHz loop bandwidth.  You can use it to compensate DPLL0. But also compensate the TDCs and AuxNCOs.
    - REFA=1Hz validation timer is at default: 10ms. It should be at least 1s=1000 ms
    If you tell me what exactly you want to accomplish with this configuration, I can help you create it. For me, it does not make sense to receive REFA=1Hz and create OUT0B=1Hz from REFB=156.25 MHz. Usually people want a 1 Hz output is phase to the 1Hz ref clock.
    Petre