AD9547 Clock Configuration File
The user requested configuration files for the AD9547 to generate output clocks of 155.52 MHz and 13.824 MHz, synchronized to an external reference clock of 1 kHz or 2 kHz. The support engineer provided a configuration file for 13.824 MHz and suggested using a 25 MHz XO as the SYSCLK input. The user also shared schematics, which were reviewed and found to be mostly correct, with a few minor adjustments recommended. The user later requested updated configuration files for 13.312 MHz and 61.44 MHz outputs.
Product Number: AD9547
Hi ADI Team,
We are planning to use AD9547BCPZ as our clock sync. As I am new to this IC could you please help me with the clock configuration file for this IC.
1. Profile 1: Output Freq 155.52MHz
2. Profile 2: Output Freq 13.824MHz
Please also suggest the Input XO frequency that we can proceed with.
We need to synchronize these output clocks with an external clock frequency of 1PPS or 2KHz.
  • Hi ADI Team, Awaiting your response.
    Just to correct "We need to synchronize these output clocks with an external clock frequency of 1KHz or 2KHz."
    Please confirm the use of 25MHz XO as SYSCLKP input frequency CB3LV-5I-25M0000-T.
  • HI,
    I'm sorry for the delay in getting back to you. We were in holiday here.
    Could you please explain to me what do you mean by synchronizing a 155.52MHz clock and a 13.824MHz clock created by a chip with an external clock of 1kHz or 2kHz?
    Petre
  • Hi Petre,
    I am attaching the schematics for your reference
    1. External Clock is 25MHz
    2. Output Clocks :
    Profile 1: 155.52MHz
    Profile 2: 13.824MHz
    3. Reference Clock:
    Case 1: 1KHz
    Case 2: 2KHz
    I meant that the output clocks from the IC need to be phase-aligned(or synced) to the reference clock inputs (1Khz/2Khz) for our case.
    PDF
  • HI,
    I am not convinced the AD9547 can do what you need. The minimum common multiplier of the 155.52MHz and 13.825MHz clocks is 622.080 MHz. This frequency is greater than the max DAC output of 450MHz. So the AD9547 cannot create these to clocks.
    I found you can use the AD9542 to create the output clocks from a 2kHz reference clock. But even this one gives me an error when I try to use 1kHz reference clock
    Petre
  • Hi Petre,
    We don't need both the clocks at the same time.
    If we configure ad9547 for 155.52Mhz then both the OUTx can generate 155.52Mhz, similar for 13.824Mhz.
  • Also, I believe this is a typo error.
    "The minimum common multiplier of the 155.52MHz and 13.825MHz clocks is 622.080 MHz. "
    It should be 13.824MHz, not 13.825MHz
    I created a configuration on an AD9548 eval board (I do not have an AD9547 eval board) and I was able to provide 1kHz at REFA and create a 155.52MHz clock at CLKOUT0. I provided a 25MHz system clock.  You can see below the AD9548 eval software window.
    I then followed the same steps and I created an AD9547 configuration. It should work. Please find it attached. Just take out the txt extension to be able to load it into the AD9547 eval software. The file contains the register values you need to load into your AD9547.
    ;Header contains information about the setup file and revision
    <Header>
    Product = AD9547
    FileVersion = 1.0
    DecimalSeparator=.    ;Used for internationalization
    </Header>
    <RegisterMap>
    &h0,&b00010000   ;10 Hex, 016 Dec
    &h1,&b00000000   ;00 Hex, 000 Dec
    &h4,&b00000000   ;00 Hex, 000 Dec
    &h5,&b00000000   ;00 Hex, 000 Dec
    &h100,&b00011000   ;18 Hex, 024 Dec
    &h101,&b00101000   ;28 Hex, 040 Dec
    &h102,&b01000101   ;45 Hex, 069 Dec
    &h103,&b01000000   ;40 Hex, 064 Dec
    &h104,&b01000010   ;42 Hex, 066 Dec
    &h105,&b00001111   ;0F Hex, 015 Dec
    &h106,&b00000001   ;01 Hex, 001 Dec
    &h107,&b00000000   ;00 Hex, 000 Dec
    &h108,&b00000000   ;00 Hex, 000 Dec
    &h200,&b00000000   ;00 Hex, 000 Dec
    &h201,&b00000000   ;00 Hex, 000 Dec
    &h202,&b00000000   ;00 Hex, 000 Dec
    &h203,&b00000000   ;00 Hex, 000 Dec
    &h204,&b00000000   ;00 Hex, 000 Dec
    &h205,&b00000000   ;00 Hex, 000 Dec
    &h206,&b00000000   ;00 Hex, 000 Dec
    &h207,&b00000000   ;00 Hex, 000 Dec
    &h208,&b00000000   ;00 Hex, 000 Dec
    &h209,&b00000000   ;00 Hex, 000 Dec
    &h20A,&b00000000   ;00 Hex, 000 Dec
    &h20B,&b00000000   ;00 Hex, 000 Dec
    &h20C,&b00000000   ;00 Hex, 000 Dec
    &h20D,&b00000000   ;00 Hex, 000 Dec
    &h20E,&b00000000   ;00 Hex, 000 Dec
    &h211,&b00000000   ;00 Hex, 000 Dec
    &h212,&b00000000   ;00 Hex, 000 Dec
    &h213,&b11111111   ;FF Hex, 255 Dec
    &h214,&b00000001   ;01 Hex, 001 Dec
    &h300,&b10111001   ;B9 Hex, 185 Dec
    &h301,&b11011111   ;DF Hex, 223 Dec
    &h302,&b10100001   ;A1 Hex, 161 Dec
    &h303,&b00101000   ;28 Hex, 040 Dec
    &h304,&b11010000   ;D0 Hex, 208 Dec
    &h305,&b00100111   ;27 Hex, 039 Dec
    &h306,&b00000000   ;00 Hex, 000 Dec
    &h307,&b00000000   ;00 Hex, 000 Dec
    &h308,&b00000000   ;00 Hex, 000 Dec
    &h309,&b00000000   ;00 Hex, 000 Dec
    &h30A,&b11111111   ;FF Hex, 255 Dec
    &h30B,&b11111111   ;FF Hex, 255 Dec
    &h30C,&b11111111   ;FF Hex, 255 Dec
    &h30D,&b00000000   ;00 Hex, 000 Dec
    &h30E,&b00000000   ;00 Hex, 000 Dec
    &h30F,&b00000000   ;00 Hex, 000 Dec
    &h310,&b00000000   ;00 Hex, 000 Dec
    &h311,&b00000000   ;00 Hex, 000 Dec
    &h312,&b00000000   ;00 Hex, 000 Dec
    &h313,&b00000000   ;00 Hex, 000 Dec
    &h314,&b11101000   ;E8 Hex, 232 Dec
    &h315,&b00000011   ;03 Hex, 003 Dec
    &h316,&b00000000   ;00 Hex, 000 Dec
    &h317,&b00000000   ;00 Hex, 000 Dec
    &h318,&b00110000   ;30 Hex, 048 Dec
    &h319,&b01110101   ;75 Hex, 117 Dec
    &h31A,&b00000000   ;00 Hex, 000 Dec
    &h31B,&b00000000   ;00 Hex, 000 Dec
    &h400,&b00001100   ;0C Hex, 012 Dec
    &h401,&b00000001   ;01 Hex, 001 Dec
    &h402,&b00000000   ;00 Hex, 000 Dec
    &h403,&b00000000   ;00 Hex, 000 Dec
    &h404,&b00000100   ;04 Hex, 004 Dec
    &h405,&b00000011   ;03 Hex, 003 Dec
    &h408,&b00000000   ;00 Hex, 000 Dec
    &h409,&b00000000   ;00 Hex, 000 Dec
    &h40A,&b00000000   ;00 Hex, 000 Dec
    &h40B,&b00000000   ;00 Hex, 000 Dec
    &h40C,&b00000000   ;00 Hex, 000 Dec
    &h40D,&b00000000   ;00 Hex, 000 Dec
    &h40E,&b00000000   ;00 Hex, 000 Dec
    &h40F,&b00000000   ;00 Hex, 000 Dec
    &h418,&b00000000   ;00 Hex, 000 Dec
    &h419,&b00000000   ;00 Hex, 000 Dec
    &h500,&b11110000   ;F0 Hex, 240 Dec
    &h501,&b00000000   ;00 Hex, 000 Dec
    &h503,&b00001000   ;08 Hex, 008 Dec
    &h504,&b00000000   ;00 Hex, 000 Dec
    &h507,&b00000000   ;00 Hex, 000 Dec
    &h600,&b00000000   ;00 Hex, 000 Dec
    &h601,&b00000000   ;00 Hex, 000 Dec
    &h602,&b00010000   ;10 Hex, 016 Dec
    &h603,&b10100101   ;A5 Hex, 165 Dec
    &h604,&b11010100   ;D4 Hex, 212 Dec
    &h605,&b11101000   ;E8 Hex, 232 Dec
    &h606,&b00000000   ;00 Hex, 000 Dec
    &h607,&b00000000   ;00 Hex, 000 Dec
    &h608,&b00010000   ;10 Hex, 016 Dec
    &h609,&b00100111   ;27 Hex, 039 Dec
    &h60A,&b00000000   ;00 Hex, 000 Dec
    &h60B,&b11101000   ;E8 Hex, 232 Dec
    &h60C,&b00000011   ;03 Hex, 003 Dec
    &h60D,&b00000000   ;00 Hex, 000 Dec
    &h60E,&b10001000   ;88 Hex, 136 Dec
    &h60F,&b00010011   ;13 Hex, 019 Dec
    &h610,&b10001000   ;88 Hex, 136 Dec
    &h611,&b00010011   ;13 Hex, 019 Dec
    &h612,&b00110110   ;36 Hex, 054 Dec
    &h613,&b10001111   ;8F Hex, 143 Dec
    &h614,&b00000000   ;00 Hex, 000 Dec
    &h615,&b01100001   ;61 Hex, 097 Dec
    &h616,&b01011100   ;5C Hex, 092 Dec
    &h617,&b00111010   ;3A Hex, 058 Dec
    &h618,&b10111011   ;BB Hex, 187 Dec
    &h619,&b00111010   ;3A Hex, 058 Dec
    &h61A,&b00011101   ;1D Hex, 029 Dec
    &h61B,&b10101010   ;AA Hex, 170 Dec
    &h61C,&b01101001   ;69 Hex, 105 Dec
    &h61D,&b00000111   ;07 Hex, 007 Dec
    &h61E,&b00000000   ;00 Hex, 000 Dec
    &h61F,&b00000000   ;00 Hex, 000 Dec
    &h620,&b00000000   ;00 Hex, 000 Dec
    &h621,&b00000000   ;00 Hex, 000 Dec
    &h622,&b01111111   ;7F Hex, 127 Dec
    &h623,&b01011111   ;5F Hex, 095 Dec
    &h624,&b00000010   ;02 Hex, 002 Dec
    &h625,&b00000000   ;00 Hex, 000 Dec
    &h626,&b00000000   ;00 Hex, 000 Dec
    &h627,&b00000000   ;00 Hex, 000 Dec
    &h628,&b00000000   ;00 Hex, 000 Dec
    &h629,&b00010000   ;10 Hex, 016 Dec
    &h62A,&b00100111   ;27 Hex, 039 Dec
    &h62B,&b00100000   ;20 Hex, 032 Dec
    &h62C,&b01000100   ;44 Hex, 068 Dec
    &h62D,&b11110100   ;F4 Hex, 244 Dec
    &h62E,&b00000001   ;01 Hex, 001 Dec
    &h62F,&b00000000   ;00 Hex, 000 Dec
    &h630,&b00100000   ;20 Hex, 032 Dec
    &h631,&b01000100   ;44 Hex, 068 Dec
    &h632,&b00000000   ;00 Hex, 000 Dec
    &h633,&b00000000   ;00 Hex, 000 Dec
    &h634,&b00000000   ;00 Hex, 000 Dec
    &h635,&b00000000   ;00 Hex, 000 Dec
    &h636,&b00000000   ;00 Hex, 000 Dec
    &h637,&b00000000   ;00 Hex, 000 Dec
    &h638,&b00000000   ;00 Hex, 000 Dec
    &h639,&b00000000   ;00 Hex, 000 Dec
    &h63A,&b00000000   ;00 Hex, 000 Dec
    &h63B,&b00000000   ;00 Hex, 000 Dec
    &h63C,&b00000000   ;00 Hex, 000 Dec
    &h63D,&b00000000   ;00 Hex, 000 Dec
    &h63E,&b00000000   ;00 Hex, 000 Dec
    &h63F,&b00000000   ;00 Hex, 000 Dec
    &h640,&b00000000   ;00 Hex, 000 Dec
    &h641,&b00000000   ;00 Hex, 000 Dec
    &h642,&b00000000   ;00 Hex, 000 Dec
    &h643,&b00000000   ;00 Hex, 000 Dec
    &h644,&b00000000   ;00 Hex, 000 Dec
    &h645,&b00000000   ;00 Hex, 000 Dec
    &h646,&b00000000   ;00 Hex, 000 Dec
    &h647,&b00000000   ;00 Hex, 000 Dec
    &h648,&b00000000   ;00 Hex, 000 Dec
    &h649,&b00000000   ;00 Hex, 000 Dec
    &h64A,&b00000000   ;00 Hex, 000 Dec
    &h64B,&b00000000   ;00 Hex, 000 Dec
    &h64C,&b00000000   ;00 Hex, 000 Dec
    &h64D,&b00000000   ;00 Hex, 000 Dec
    &h64E,&b00000000   ;00 Hex, 000 Dec
    &h64F,&b00000000   ;00 Hex, 000 Dec
    &h650,&b00000000   ;00 Hex, 000 Dec
    &h651,&b00000000   ;00 Hex, 000 Dec
    &h652,&b00000000   ;00 Hex, 000 Dec
    &h653,&b00000000   ;00 Hex, 000 Dec
    &h654,&b00000000   ;00 Hex, 000 Dec
    &h655,&b00000000   ;00 Hex, 000 Dec
    &h656,&b00000000   ;00 Hex, 000 Dec
    &h657,&b00000000   ;00 Hex, 000 Dec
    &h658,&b00000000   ;00 Hex, 000 Dec
    &h659,&b00000000   ;00 Hex, 000 Dec
    &h65A,&b00000000   ;00 Hex, 000 Dec
    &h65B,&b00000000   ;00 Hex, 000 Dec
    &h65C,&b00000000   ;00 Hex, 000 Dec
    &h65D,&b00000000   ;00 Hex, 000 Dec
    &h65E,&b00000000   ;00 Hex, 000 Dec
    &h65F,&b00000000   ;00 Hex, 000 Dec
    &h660,&b00000000   ;00 Hex, 000 Dec
    &h661,&b00000000   ;00 Hex, 000 Dec
    &h662,&b00000000   ;00 Hex, 000 Dec
    &h663,&b00000000   ;00 Hex, 000 Dec
    &h680,&b00000000   ;00 Hex, 000 Dec
    &h681,&b00000000   ;00 Hex, 000 Dec
    &h682,&b00000000   ;00 Hex, 000 Dec
    &h683,&b00000000   ;00 Hex, 000 Dec
    &h684,&b00000000   ;00 Hex, 000 Dec
    &h685,&b00000000   ;00 Hex, 000 Dec
    &h686,&b00000000   ;00 Hex, 000 Dec
    &h687,&b00000000   ;00 Hex, 000 Dec
    &h688,&b00000000   ;00 Hex, 000 Dec
    &h689,&b00000000   ;00 Hex, 000 Dec
    &h68A,&b00000000   ;00 Hex, 000 Dec
    &h68B,&b00000000   ;00 Hex, 000 Dec
    &h68C,&b00000000   ;00 Hex, 000 Dec
    &h68D,&b00000000   ;00 Hex, 000 Dec
    &h68E,&b00000000   ;00 Hex, 000 Dec
    &h68F,&b00000000   ;00 Hex, 000 Dec
    &h690,&b00000000   ;00 Hex, 000 Dec
    &h691,&b00000000   ;00 Hex, 000 Dec
    &h692,&b00000000   ;00 Hex, 000 Dec
    &h693,&b00000000   ;00 Hex, 000 Dec
    &h694,&b00000000   ;00 Hex, 000 Dec
    &h695,&b00000000   ;00 Hex, 000 Dec
    &h696,&b00000000   ;00 Hex, 000 Dec
    &h697,&b00000000   ;00 Hex, 000 Dec
    &h698,&b00000000   ;00 Hex, 000 Dec
    &h699,&b00000000   ;00 Hex, 000 Dec
    &h69A,&b00000000   ;00 Hex, 000 Dec
    &h69B,&b00000000   ;00 Hex, 000 Dec
    &h69C,&b00000000   ;00 Hex, 000 Dec
    &h69D,&b00000000   ;00 Hex, 000 Dec
    &h69E,&b00000000   ;00 Hex, 000 Dec
    &h69F,&b00000000   ;00 Hex, 000 Dec
    &h6A0,&b00000000   ;00 Hex, 000 Dec
    &h6A1,&b00000000   ;00 Hex, 000 Dec
    &h6A2,&b00000000   ;00 Hex, 000 Dec
    &h6A3,&b00000000   ;00 Hex, 000 Dec
    &h6A4,&b00000000   ;00 Hex, 000 Dec
    &h6A5,&b00000000   ;00 Hex, 000 Dec
    &h6A6,&b00000000   ;00 Hex, 000 Dec
    &h6A7,&b00000000   ;00 Hex, 000 Dec
    &h6A8,&b00000000   ;00 Hex, 000 Dec
    &h6A9,&b00000000   ;00 Hex, 000 Dec
    &h6AA,&b00000000   ;00 Hex, 000 Dec
    &h6AB,&b00000000   ;00 Hex, 000 Dec
    &h6AC,&b00000000   ;00 Hex, 000 Dec
    &h6AD,&b00000000   ;00 Hex, 000 Dec
    &h6AE,&b00000000   ;00 Hex, 000 Dec
    &h6AF,&b00000000   ;00 Hex, 000 Dec
    &h6B0,&b00000000   ;00 Hex, 000 Dec
    &h6B1,&b00000000   ;00 Hex, 000 Dec
    &h6B2,&b00000000   ;00 Hex, 000 Dec
    &h6B3,&b00000000   ;00 Hex, 000 Dec
    &h6B4,&b00000000   ;00 Hex, 000 Dec
    &h6B5,&b00000000   ;00 Hex, 000 Dec
    &h6B6,&b00000000   ;00 Hex, 000 Dec
    &h6B7,&b00000000   ;00 Hex, 000 Dec
    &h6B8,&b00000000   ;00 Hex, 000 Dec
    &h6B9,&b00000000   ;00 Hex, 000 Dec
    &h6BA,&b00000000   ;00 Hex, 000 Dec
    &h6BB,&b00000000   ;00 Hex, 000 Dec
    &h6BC,&b00000000   ;00 Hex, 000 Dec
    &h6BD,&b00000000   ;00 Hex, 000 Dec
    &h6BE,&b00000000   ;00 Hex, 000 Dec
    &h6BF,&b00000000   ;00 Hex, 000 Dec
    &h6C0,&b00000000   ;00 Hex, 000 Dec
    &h6C1,&b00000000   ;00 Hex, 000 Dec
    &h6C2,&b00000000   ;00 Hex, 000 Dec
    &h6C3,&b00000000   ;00 Hex, 000 Dec
    &h6C4,&b00000000   ;00 Hex, 000 Dec
    &h6C5,&b00000000   ;00 Hex, 000 Dec
    &h6C6,&b00000000   ;00 Hex, 000 Dec
    &h6C7,&b00000000   ;00 Hex, 000 Dec
    &h6C8,&b00000000   ;00 Hex, 000 Dec
    &h6C9,&b00000000   ;00 Hex, 000 Dec
    &h6CA,&b00000000   ;00 Hex, 000 Dec
    &h6CB,&b00000000   ;00 Hex, 000 Dec
    &h6CC,&b00000000   ;00 Hex, 000 Dec
    &h6CD,&b00000000   ;00 Hex, 000 Dec
    &h6CE,&b00000000   ;00 Hex, 000 Dec
    &h6CF,&b00000000   ;00 Hex, 000 Dec
    &h6D0,&b00000000   ;00 Hex, 000 Dec
    &h6D1,&b00000000   ;00 Hex, 000 Dec
    &h6D2,&b00000000   ;00 Hex, 000 Dec
    &h6D3,&b00000000   ;00 Hex, 000 Dec
    &h6D4,&b00000000   ;00 Hex, 000 Dec
    &h6D5,&b00000000   ;00 Hex, 000 Dec
    &h6D6,&b00000000   ;00 Hex, 000 Dec
    &h6D7,&b00000000   ;00 Hex, 000 Dec
    &h6D8,&b00000000   ;00 Hex, 000 Dec
    &h6D9,&b00000000   ;00 Hex, 000 Dec
    &h6DA,&b00000000   ;00 Hex, 000 Dec
    &h6DB,&b00000000   ;00 Hex, 000 Dec
    &h6DC,&b00000000   ;00 Hex, 000 Dec
    &h6DD,&b00000000   ;00 Hex, 000 Dec
    &h6DE,&b00000000   ;00 Hex, 000 Dec
    &h6DF,&b00000000   ;00 Hex, 000 Dec
    &h6E0,&b00000000   ;00 Hex, 000 Dec
    &h6E1,&b00000000   ;00 Hex, 000 Dec
    &h6E2,&b00000000   ;00 Hex, 000 Dec
    &h6E3,&b00000000   ;00 Hex, 000 Dec
    &h700,&b00000000   ;00 Hex, 000 Dec
    &h701,&b00000000   ;00 Hex, 000 Dec
    &h702,&b00000000   ;00 Hex, 000 Dec
    &h703,&b00000000   ;00 Hex, 000 Dec
    &h704,&b00000000   ;00 Hex, 000 Dec
    &h705,&b00000000   ;00 Hex, 000 Dec
    &h706,&b00000000   ;00 Hex, 000 Dec
    &h707,&b00000000   ;00 Hex, 000 Dec
    &h708,&b00000000   ;00 Hex, 000 Dec
    &h709,&b00000000   ;00 Hex, 000 Dec
    &h70A,&b00000000   ;00 Hex, 000 Dec
    &h70B,&b00000000   ;00 Hex, 000 Dec
    &h70C,&b00000000   ;00 Hex, 000 Dec
    &h70D,&b00000000   ;00 Hex, 000 Dec
    &h70E,&b00000000   ;00 Hex, 000 Dec
    &h70F,&b00000000   ;00 Hex, 000 Dec
    &h710,&b00000000   ;00 Hex, 000 Dec
    &h711,&b00000000   ;00 Hex, 000 Dec
    &h712,&b00000000   ;00 Hex, 000 Dec
    &h713,&b00000000   ;00 Hex, 000 Dec
    &h714,&b00000000   ;00 Hex, 000 Dec
    &h715,&b00000000   ;00 Hex, 000 Dec
    &h716,&b00000000   ;00 Hex, 000 Dec
    &h717,&b00000000   ;00 Hex, 000 Dec
    &h718,&b00000000   ;00 Hex, 000 Dec
    &h719,&b00000000   ;00 Hex, 000 Dec
    &h71A,&b00000000   ;00 Hex, 000 Dec
    &h71B,&b00000000   ;00 Hex, 000 Dec
    &h71C,&b00000000   ;00 Hex, 000 Dec
    &h71D,&b00000000   ;00 Hex, 000 Dec
    &h71E,&b00000000   ;00 Hex, 000 Dec
    &h71F,&b00000000   ;00 Hex, 000 Dec
    &h720,&b00000000   ;00 Hex, 000 Dec
    &h721,&b00000000   ;00 Hex, 000 Dec
    &h722,&b00000000   ;00 Hex, 000 Dec
    &h723,&b00000000   ;00 Hex, 000 Dec
    &h724,&b00000000   ;00 Hex, 000 Dec
    &h725,&b00000000   ;00 Hex, 000 Dec
    &h726,&b00000000   ;00 Hex, 000 Dec
    &h727,&b00000000   ;00 Hex, 000 Dec
    &h728,&b00000000   ;00 Hex, 000 Dec
    &h729,&b00000000   ;00 Hex, 000 Dec
    &h72A,&b00000000   ;00 Hex, 000 Dec
    &h72B,&b00000000   ;00 Hex, 000 Dec
    &h72C,&b00000000   ;00 Hex, 000 Dec
    &h72D,&b00000000   ;00 Hex, 000 Dec
    &h72E,&b00000000   ;00 Hex, 000 Dec
    &h72F,&b00000000   ;00 Hex, 000 Dec
    &h730,&b00000000   ;00 Hex, 000 Dec
    &h731,&b00000000   ;00 Hex, 000 Dec
    &h732,&b00000000   ;00 Hex, 000 Dec
    &h733,&b00000000   ;00 Hex, 000 Dec
    &h734,&b00000000   ;00 Hex, 000 Dec
    &h735,&b00000000   ;00 Hex, 000 Dec
    &h736,&b00000000   ;00 Hex, 000 Dec
    &h737,&b00000000   ;00 Hex, 000 Dec
    &h738,&b00000000   ;00 Hex, 000 Dec
    &h739,&b00000000   ;00 Hex, 000 Dec
    &h73A,&b00000000   ;00 Hex, 000 Dec
    &h73B,&b00000000   ;00 Hex, 000 Dec
    &h73C,&b00000000   ;00 Hex, 000 Dec
    &h73D,&b00000000   ;00 Hex, 000 Dec
    &h73E,&b00000000   ;00 Hex, 000 Dec
    &h73F,&b00000000   ;00 Hex, 000 Dec
    &h740,&b00000000   ;00 Hex, 000 Dec
    &h741,&b00000000   ;00 Hex, 000 Dec
    &h742,&b00000000   ;00 Hex, 000 Dec
    &h743,&b00000000   ;00 Hex, 000 Dec
    &h744,&b00000000   ;00 Hex, 000 Dec
    &h745,&b00000000   ;00 Hex, 000 Dec
    &h746,&b00000000   ;00 Hex, 000 Dec
    &h747,&b00000000   ;00 Hex, 000 Dec
    &h748,&b00000000   ;00 Hex, 000 Dec
    &h749,&b00000000   ;00 Hex, 000 Dec
    &h74A,&b00000000   ;00 Hex, 000 Dec
    &h74B,&b00000000   ;00 Hex, 000 Dec
    &h74C,&b00000000   ;00 Hex, 000 Dec
    &h74D,&b00000000   ;00 Hex, 000 Dec
    &h74E,&b00000000   ;00 Hex, 000 Dec
    &h74F,&b00000000   ;00 Hex, 000 Dec
    &h750,&b00000000   ;00 Hex, 000 Dec
    &h751,&b00000000   ;00 Hex, 000 Dec
    &h752,&b00000000   ;00 Hex, 000 Dec
    &h753,&b00000000   ;00 Hex, 000 Dec
    &h754,&b00000000   ;00 Hex, 000 Dec
    &h755,&b00000000   ;00 Hex, 000 Dec
    &h756,&b00000000   ;00 Hex, 000 Dec
    &h757,&b00000000   ;00 Hex, 000 Dec
    &h758,&b00000000   ;00 Hex, 000 Dec
    &h759,&b00000000   ;00 Hex, 000 Dec
    &h75A,&b00000000   ;00 Hex, 000 Dec
    &h75B,&b00000000   ;00 Hex, 000 Dec
    &h75C,&b00000000   ;00 Hex, 000 Dec
    &h75D,&b00000000   ;00 Hex, 000 Dec
    &h75E,&b00000000   ;00 Hex, 000 Dec
    &h75F,&b00000000   ;00 Hex, 000 Dec
    &h760,&b00000000   ;00 Hex, 000 Dec
    &h761,&b00000000   ;00 Hex, 000 Dec
    &h762,&b00000000   ;00 Hex, 000 Dec
    &h763,&b00000000   ;00 Hex, 000 Dec
    &h780,&b00000000   ;00 Hex, 000 Dec
    &h781,&b00000000   ;00 Hex, 000 Dec
    &h782,&b00000000   ;00 Hex, 000 Dec
    &h783,&b00000000   ;00 Hex, 000 Dec
    &h784,&b00000000   ;00 Hex, 000 Dec
    &h785,&b00000000   ;00 Hex, 000 Dec
    &h786,&b00000000   ;00 Hex, 000 Dec
    &h787,&b00000000   ;00 Hex, 000 Dec
    &h788,&b00000000   ;00 Hex, 000 Dec
    &h789,&b00000000   ;00 Hex, 000 Dec
    &h78A,&b00000000   ;00 Hex, 000 Dec
    &h78B,&b00000000   ;00 Hex, 000 Dec
    &h78C,&b00000000   ;00 Hex, 000 Dec
    &h78D,&b00000000   ;00 Hex, 000 Dec
    &h78E,&b00000000   ;00 Hex, 000 Dec
    &h78F,&b00000000   ;00 Hex, 000 Dec
    &h790,&b00000000   ;00 Hex, 000 Dec
    &h791,&b00000000   ;00 Hex, 000 Dec
    &h792,&b00000000   ;00 Hex, 000 Dec
    &h793,&b00000000   ;00 Hex, 000 Dec
    &h794,&b00000000   ;00 Hex, 000 Dec
    &h795,&b00000000   ;00 Hex, 000 Dec
    &h796,&b00000000   ;00 Hex, 000 Dec
    &h797,&b00000000   ;00 Hex, 000 Dec
    &h798,&b00000000   ;00 Hex, 000 Dec
    &h799,&b00000000   ;00 Hex, 000 Dec
    &h79A,&b00000000   ;00 Hex, 000 Dec
    &h79B,&b00000000   ;00 Hex, 000 Dec
    &h79C,&b00000000   ;00 Hex, 000 Dec
    &h79D,&b00000000   ;00 Hex, 000 Dec
    &h79E,&b00000000   ;00 Hex, 000 Dec
    &h79F,&b00000000   ;00 Hex, 000 Dec
    &h7A0,&b00000000   ;00 Hex, 000 Dec
    &h7A1,&b00000000   ;00 Hex, 000 Dec
    &h7A2,&b00000000   ;00 Hex, 000 Dec
    &h7A3,&b00000000   ;00 Hex, 000 Dec
    &h7A4,&b00000000   ;00 Hex, 000 Dec
    &h7A5,&b00000000   ;00 Hex, 000 Dec
    &h7A6,&b00000000   ;00 Hex, 000 Dec
    &h7A7,&b00000000   ;00 Hex, 000 Dec
    &h7A8,&b00000000   ;00 Hex, 000 Dec
    &h7A9,&b00000000   ;00 Hex, 000 Dec
    &h7AA,&b00000000   ;00 Hex, 000 Dec
    &h7AB,&b00000000   ;00 Hex, 000 Dec
    &h7AC,&b00000000   ;00 Hex, 000 Dec
    &h7AD,&b00000000   ;00 Hex, 000 Dec
    &h7AE,&b00000000   ;00 Hex, 000 Dec
    &h7AF,&b00000000   ;00 Hex, 000 Dec
    &h7B0,&b00000000   ;00 Hex, 000 Dec
    &h7B1,&b00000000   ;00 Hex, 000 Dec
    &h7B2,&b00000000   ;00 Hex, 000 Dec
    &h7B3,&b00000000   ;00 Hex, 000 Dec
    &h7B4,&b00000000   ;00 Hex, 000 Dec
    &h7B5,&b00000000   ;00 Hex, 000 Dec
    &h7B6,&b00000000   ;00 Hex, 000 Dec
    &h7B7,&b00000000   ;00 Hex, 000 Dec
    &h7B8,&b00000000   ;00 Hex, 000 Dec
    &h7B9,&b00000000   ;00 Hex, 000 Dec
    &h7BA,&b00000000   ;00 Hex, 000 Dec
    &h7BB,&b00000000   ;00 Hex, 000 Dec
    &h7BC,&b00000000   ;00 Hex, 000 Dec
    &h7BD,&b00000000   ;00 Hex, 000 Dec
    &h7BE,&b00000000   ;00 Hex, 000 Dec
    &h7BF,&b00000000   ;00 Hex, 000 Dec
    &h7C0,&b00000000   ;00 Hex, 000 Dec
    &h7C1,&b00000000   ;00 Hex, 000 Dec
    &h7C2,&b00000000   ;00 Hex, 000 Dec
    &h7C3,&b00000000   ;00 Hex, 000 Dec
    &h7C4,&b00000000   ;00 Hex, 000 Dec
    &h7C5,&b00000000   ;00 Hex, 000 Dec
    &h7C6,&b00000000   ;00 Hex, 000 Dec
    &h7C7,&b00000000   ;00 Hex, 000 Dec
    &h7C8,&b00000000   ;00 Hex, 000 Dec
    &h7C9,&b00000000   ;00 Hex, 000 Dec
    &h7CA,&b00000000   ;00 Hex, 000 Dec
    &h7CB,&b00000000   ;00 Hex, 000 Dec
    &h7CC,&b00000000   ;00 Hex, 000 Dec
    &h7CD,&b00000000   ;00 Hex, 000 Dec
    &h7CE,&b00000000   ;00 Hex, 000 Dec
    &h7CF,&b00000000   ;00 Hex, 000 Dec
    &h7D0,&b00000000   ;00 Hex, 000 Dec
    &h7D1,&b00000000   ;00 Hex, 000 Dec
    &h7D2,&b00000000   ;00 Hex, 000 Dec
    &h7D3,&b00000000   ;00 Hex, 000 Dec
    &h7D4,&b00000000   ;00 Hex, 000 Dec
    &h7D5,&b00000000   ;00 Hex, 000 Dec
    &h7D6,&b00000000   ;00 Hex, 000 Dec
    &h7D7,&b00000000   ;00 Hex, 000 Dec
    &h7D8,&b00000000   ;00 Hex, 000 Dec
    &h7D9,&b00000000   ;00 Hex, 000 Dec
    &h7DA,&b00000000   ;00 Hex, 000 Dec
    &h7DB,&b00000000   ;00 Hex, 000 Dec
    &h7DC,&b00000000   ;00 Hex, 000 Dec
    &h7DD,&b00000000   ;00 Hex, 000 Dec
    &h7DE,&b00000000   ;00 Hex, 000 Dec
    &h7DF,&b00000000   ;00 Hex, 000 Dec
    &h7E0,&b00000000   ;00 Hex, 000 Dec
    &h7E1,&b00000000   ;00 Hex, 000 Dec
    &h7E2,&b00000000   ;00 Hex, 000 Dec
    &h7E3,&b00000000   ;00 Hex, 000 Dec
    &hA00,&b00000000   ;00 Hex, 000 Dec
    &hA01,&b00000000   ;00 Hex, 000 Dec
    &hA02,&b00000000   ;00 Hex, 000 Dec
    &hA03,&b00000000   ;00 Hex, 000 Dec
    &hA04,&b00000000   ;00 Hex, 000 Dec
    &hA05,&b00000000   ;00 Hex, 000 Dec
    &hA06,&b00000000   ;00 Hex, 000 Dec
    &hA07,&b00000000   ;00 Hex, 000 Dec
    &hA08,&b00000000   ;00 Hex, 000 Dec
    &hA09,&b00000000   ;00 Hex, 000 Dec
    &hA0C,&b00000000   ;00 Hex, 000 Dec
    &hA0D,&b00000000   ;00 Hex, 000 Dec
    &hA0E,&b00000000   ;00 Hex, 000 Dec
    &hA0F,&b00000000   ;00 Hex, 000 Dec
    &hA10,&b00000000   ;00 Hex, 000 Dec
    &hE00,&b00000000   ;00 Hex, 000 Dec
    &hE01,&b00000000   ;00 Hex, 000 Dec
    &hE02,&b00000000   ;00 Hex, 000 Dec
    &hE03,&b00000000   ;00 Hex, 000 Dec
    &hE10,&b00001000   ;08 Hex, 008 Dec
    &hE11,&b00000001   ;01 Hex, 001 Dec
    &hE12,&b00000000   ;00 Hex, 000 Dec
    &hE13,&b10000000   ;80 Hex, 128 Dec
    &hE14,&b10100000   ;A0 Hex, 160 Dec
    &hE15,&b00010100   ;14 Hex, 020 Dec
    &hE16,&b00000010   ;02 Hex, 002 Dec
    &hE17,&b00000000   ;00 Hex, 000 Dec
    &hE18,&b00011011   ;1B Hex, 027 Dec
    &hE19,&b00000011   ;03 Hex, 003 Dec
    &hE1A,&b00000000   ;00 Hex, 000 Dec
    &hE1B,&b00011001   ;19 Hex, 025 Dec
    &hE1C,&b00000100   ;04 Hex, 004 Dec
    &hE1D,&b00000000   ;00 Hex, 000 Dec
    &hE1E,&b10000000   ;80 Hex, 128 Dec
    &hE1F,&b00000111   ;07 Hex, 007 Dec
    &hE20,&b00000101   ;05 Hex, 005 Dec
    &hE21,&b00000000   ;00 Hex, 000 Dec
    &hE22,&b01100011   ;63 Hex, 099 Dec
    &hE23,&b00000110   ;06 Hex, 006 Dec
    &hE24,&b00000000   ;00 Hex, 000 Dec
    &hE25,&b01100011   ;63 Hex, 099 Dec
    &hE26,&b00000110   ;06 Hex, 006 Dec
    &hE27,&b10000000   ;80 Hex, 128 Dec
    &hE28,&b01100011   ;63 Hex, 099 Dec
    &hE29,&b00000111   ;07 Hex, 007 Dec
    &hE2A,&b00000000   ;00 Hex, 000 Dec
    &hE2B,&b01100011   ;63 Hex, 099 Dec
    &hE2C,&b00000111   ;07 Hex, 007 Dec
    &hE2D,&b10000000   ;80 Hex, 128 Dec
    &hE2E,&b10000000   ;80 Hex, 128 Dec
    &hE2F,&b00010000   ;10 Hex, 016 Dec
    &hE30,&b00001010   ;0A Hex, 010 Dec
    &hE31,&b00000000   ;00 Hex, 000 Dec
    &hE32,&b10000000   ;80 Hex, 128 Dec
    &hE33,&b11111111   ;FF Hex, 255 Dec
    &hE34,&b00000000   ;00 Hex, 000 Dec
    &hE35,&b00000000   ;00 Hex, 000 Dec
    &hE36,&b00000000   ;00 Hex, 000 Dec
    &hE37,&b00000000   ;00 Hex, 000 Dec
    &hE38,&b00000000   ;00 Hex, 000 Dec
    &hE39,&b00000000   ;00 Hex, 000 Dec
    &hE3A,&b00000000   ;00 Hex, 000 Dec
    &hE3B,&b00000000   ;00 Hex, 000 Dec
    &hE3C,&b00000000   ;00 Hex, 000 Dec
    &hE3D,&b00000000   ;00 Hex, 000 Dec
    &hE3E,&b00000000   ;00 Hex, 000 Dec
    &hE3F,&b00000000   ;00 Hex, 000 Dec
    </RegisterMap>
    <PinStates>
    MPins=&h0
    </PinStates>
    <SoftwareSettings>
    AutoIOUpdate=1              ;AutoIOUpdate Setting
    OverRideJumpersONReset=0    ;1 = Override M-Pin Jumper Settings, 0 = Use M-Pin Jumper Settings
    MPinStatesDuringReset=&h0   ;M-Pin States to be applied to the M-Pins durring a reset
    ExternalClock=25    ;External Clock Frequency in MHz
    </SoftwareSettings>
    Petre
  • Hi Petre,
    Could you please help to share the file for the Output clock of 13.824MHz?
    In 155.52.txt file,
    Here,
    the Auto Sync Mode is disable > Do this needs to be set to SYNC ON DPLL PHASE LOCK to sync with ref clock of 1KHz?
    Similarly Sync Source do I need to set to reference?
    Please find attached an AD9547 configuration that receives 2kHz at REFA and creates 13.824MHz at CLKOUT0. I'll let you develop the other permutations.
    <Header>
    Product = AD9547
    FileVersion = 1.0
    </Header>
    <RegisterMap>
    &h300,&b11000001   ;C1 Hex, 193 Dec
    &h301,&b11111111   ;FF Hex, 255 Dec
    &h302,&b01010110   ;56 Hex, 086 Dec
    &h303,&b10110010   ;B2 Hex, 178 Dec
    &h304,&b01100011   ;63 Hex, 099 Dec
    &h305,&b00100011   ;23 Hex, 035 Dec
    &h408,&b00001001   ;09 Hex, 009 Dec
    &h602,&b10001000   ;88 Hex, 136 Dec
    &h603,&b01010010   ;52 Hex, 082 Dec
    &h604,&b01101010   ;6A Hex, 106 Dec
    &h605,&b01110100   ;74 Hex, 116 Dec
    &h612,&b10011000   ;98 Hex, 152 Dec
    &h613,&b11111110   ;FE Hex, 254 Dec
    &h614,&b11000000   ;C0 Hex, 192 Dec
    &h615,&b01100000   ;60 Hex, 096 Dec
    &h622,&b11111111   ;FF Hex, 255 Dec
    &h623,&b00011011   ;1B Hex, 027 Dec
    </RegisterMap>
    <PinStates>
    MPins=&h0
    </PinStates>
    <SoftwareSettings>
    </SoftwareSettings>
    Regarding the sync modes: When the sync source is direct (the default 00 bits 5:4 in register 0x0402), this means one has to manipulate the bit 1 in register 0x0A02 to sync the outputs. Clearly, the AD9548 eval software generates isync automatically because I got the output clock with Auto sync mode disabled and Sync Source=direct.
    I recommend reading the sections Clock Distribution Synchronization and Active Reference Synchronization starting at page 51 in rev G data sheet.
    Petre
  • Thanks Petre,
    I will look into this.
    Could you please help to review the schematics I shared. Your review comments would be helpful.